Generator Overvoltage Relay (59 G)


Overvoltage shouldn’t occur ** a Generator fitted with an automatic voltage regulator. Overvoltage may be caused by defective operati** of the voltage regulator under isolated operati** of the generator. The relay detects the over excitati** of generators and transformers by measuring the over voltage.









Data for setting calculati**

Generator Voltage------------------------------------19000 V
VT turns ratio ----------------------------------------19000 / 100 V = 190
The max. permissible voltage for c**tinuous load operati** --- 105 %
The max. permissible voltage for no-load operati** -------------- 110 %
The max. permissible transient overvoltage ------------------------ 120 %



Relay Setting


1- Setting C**diti**s

The trip pickup is intended for moderate overvoltage of l**g durati**.
Pickup < The max. Permissible transient overvoltage .
= 19000 / 190 * 1.20
= 120 V
2- Settings
Channel
Pickup
Delay
Functi**
#1
106 %
2.5 Sec.
Alarm
#2
110 %
40 Sec.
Trip
#3
120 %
3 Sec.
Trip