عرض مشاركة واحدة
  #1  
قديم 01-01-2011, 07:05 PM
الصورة الرمزية Khaled Hamza
Khaled Hamza Khaled Hamza غير متواجد حالياً
عضو فعال
 
تاريخ التسجيل: Aug 2010
الدولة: Egypt
المشاركات: 68
معدل تقييم المستوى: 14
Khaled Hamza is on a distinguished road
Lightbulb Generator over Fluxing Relay (24G


Generator over Fluxing Relay (24G)


-The relay measures the ratio of voltage to frequency (V/Hz) as this ratio is proporti**al to the flux-density level of the electromagnetic machine.

-Over Fluxing (Over Excitati**) may be occur when a Generator is ** an isolated operati** with the AVR in service and the generator speed decreasing from the synchr**ous speed.
-Over Fluxing may also be occurring when the utility system frequency decreases to a low value by any reas**.






There are two sets of the V/Hz relays are provided for Generator Protecti**:-


A) Relay 24G (#2) for alarm

A definite time element #2 of the relay will be used to provide an alarm.
B) Relay 24G (#1 & INV) for trip
Operati** of the relay 24G will trip the switchyard breaker.
An inverse time element of the relay will be used to provide a trip c**tact and a definite time element #1 is also used to further shape the protecti** curves.

Data for setting calculati**s
Short-time V/Hz withstand level at full load -----120%
C**tinuous V/Hz withstand level at full load-----105%
AVR V/Hz limiter setting -----------------------------105%




Setting of generator V/Hz alarm relay 24G (#2)

1)V/Hz alarm setting
Setting < c**tinuous V/Hz withstand level at full load = 105 %
2)V/Hz alarm delay
Setting = 30 cycles (0.6 Sec.)






Setting of generator V/Hz alarm relay 24G (INV)

1) V/Hz trip setting for inverse time element
Setting = 107 %
2) V/Hz Reset rate for inverse time element
Reset rate = Practical recommendati** is minimum setpoint of the relay
Setting = 1 Sec.

NOTE!! “If the generator is synchr**ized immediately after tripping by V/Hz relay operati**, the generator will be damaged under V/Hz c**diti** before limitati** value. “


Setting of generator V/Hz alarm relay 24G (#1)
1)V/Hz alarm setting
Setting < short V/Hz withstand level at full load = 120 %


2)V/Hz alarm delay
Setting = 50 cycles (1 Sec.)


Google+

شارك إعجابك بالموضوع --» 

رد مع اقتباس